Zone stays on as long as wiires is connected

Post by kknisley »

One of my zones stays on if the wire remains connected to the controller, no matter if the controller is on or off. When I disconnect the wire, the zone turns off.

It appears as though the connection at the controller is still charged, even when off. I replaced the controller board once already with no change in status,

Any ideas?

Topic Author
kknisley
Posts: 2
Joined: Fri Oct 16, 2020 10:12 am
Location: Tallahassee, Florida
Grass Type: Centipede
Lawn Size: 1.5 acres
Mower: Scag Freedom Z 52"

Re: Zone stays on as long as wires is connected

Post by kknisley »

Hunter Pro C

RVAGuy
Posts: 134
Joined: Mon Jul 27, 2020 5:49 pm
Location: Richmond, VA
Grass Type: Tall Fescue / KBG
Lawn Size: 8,100 sf
Mower: Honda HRX217HYA

Re: Zone stays on as long as wiires is connected

Post by RVAGuy »

Disconnect the wire from controller and see if it's hot at the wire or the terminal of the controller. If it's hot at the terminal of the controller with it off, you need a new controller.